new screed

Discussion in 'Subfloor Preparation' started by dazza, Mar 8, 2014.

  1. dazza

    dazza Well-Known Member

    698
    103
    43
    Went to see a job a few days ago wet underfloor heating system 7 inches of screed been down 6 weeks alarm bells ringing. I've checked it with the mrh3 in masonry mode that was reading 71 so set up some boxes and left them for 4 days I've gone back today with subfloor temp 20.5 and rh 90.5 with hygomaster. How long do you think I should tell the client to leave it? Engineered floated is going down.
     
  2. merit

    merit Well-Known Member

    8,220
    1,679
    113
    Until it reads 75% lol
     
  3. bournemouth

    bournemouth Super Moderator

    2,015
    766
    113
    20.5 is the ufh still on ? cant test is ufh is on
     
  4. dazza

    dazza Well-Known Member

    698
    103
    43
    ufh isn't on. I did check. Been sunny for once and its a conservatory.
     
  5. dazza

    dazza Well-Known Member

    698
    103
    43
    Cheers merit. :D
     
  6. mjfl

    mjfl Well-Known Member

    6,259
    1,593
    113
    on average I have found them to drop by 2% a week with good ventilation and a bit of heat, obviously not from the floor ...lol
     