Problems with karndean

Discussion in 'Vinyl / Impervious floor coverings' started by Carys, Mar 24, 2015.

  1. Carys

    Carys Member

    18
    1
    3
    Can anyone help please?
    We have had karndean fitted in our home by very experienced fitter in November 2014 over most of ground floor. It is an old house which had a lot of rising damp so builder dug up old floors and installed damp course and new floor with underfloor heating. The subfloor was poured over underfloor heating pipes and heating left on for 4-6 weeks before fitter was happy that moisture levels had come down to acceptable level. He came over every week to measure with a hand held device. He then painted a green coloured primer over subfloor and then latex before gluing karndean on. The job looked great until we noticed karndean lifting, initially under 4 doors between rooms. When tiles lifted, latex had stuck to tile but had lifted from the subfloor. There was a crack in the subfloor under 3 of the doors and installer thought this was cause of karndean lifting as there was no dampness. However, it has now lifted in two more places :the hall ( away from any door) and again latex stuck on karndean but has come off the floor. it is also lfiting at one edge but here the tile has lifted from the latex and the latex is stuck to the floor. He has checked moisture levels again with hand held device and they are just about ok. There is no visible dampness on tiles or subfloor and no damp smell. he says he will use another more sophisticated device now to measure the moisture which has to be left for two days to take a reading. We are all baffled....any suggestions welcome.
    Thank you
     
  2. Trimmer

    Trimmer Well-Known Member

    1,464
    490
    83
    Find out what screed the builder put over the underfloor heating pipes.
     
  3. merit

    merit Well-Known Member

    8,003
    1,640
    113
    Was it a liquid cement? How deep was it poured?
     
  4. Carys

    Carys Member

    18
    1
    3
    Anhydrite sceed came ready mixed and applied from hose
     
  5. pf flooring

    pf flooring Well-Known Member

    1,600
    602
    113
    did he grind it?
     
  6. DM Flooring

    DM Flooring Well-Known Member

    1,045
    395
    83
    What screed/primer did he use over the Anhydrite as in make and manufacturer. Can only use certain screeds over Anhydrite.
     
  7. Spacey

    Spacey Super Moderator Staff Member

    6,516
    1,878
    113
    By the sound if it he didn't ?
     
  8. Spacey

    Spacey Super Moderator Staff Member

    6,516
    1,878
    113
    Pl31 I'd say Dave Not suitable

    But if the fitter aint grinded the top off its going to fail anyway
     
  9. DM Flooring

    DM Flooring Well-Known Member

    1,045
    395
    83
    I know but be interesting to found out what materials were used.
     
  10. Carys

    Carys Member

    18
    1
    3
    Not grinder used just painted a green primer on then latex but don't know what type.
     
  11. Trimmer

    Trimmer Well-Known Member

    1,464
    490
    83
    Check with the builder what type of screed was pumped in. This is essential information.

    If we don't know then we're just guessing. Most of us suspect what the problem is and the cause but we have to know what screed was pumped in. Otherwise we could give advice that is incorrect.
     
  12. Bow Flooring

    Bow Flooring Well-Known Member

    114
    70
    28
    They said anhydrite trimmer
     
  13. merit

    merit Well-Known Member

    8,003
    1,640
    113
    Anhydrate mr Trimmer or are you wanting specific manufacturers? A surface scanning moisture meter is useless on these
     
  14. Bow Flooring

    Bow Flooring Well-Known Member

    114
    70
    28
    Needs to be grinded to remove the lattice which happens during drying
    The lattice should also be removed to aid drying
     
  15. pf flooring

    pf flooring Well-Known Member

    1,600
    602
    113
    P131 has been used unless anybody else knows of another green primer, id also bet top dollar that he has used a cement based screed too, could be/probably the case that the fitter didn't realise what he was up against!
     
  16. Trimmer

    Trimmer Well-Known Member

    1,464
    490
    83
    Oops. Just reread thread.

    P131 is a common green primer. Not compatible with anhydrite though.
     
  17. hobbit

    hobbit Well-Known Member

    502
    223
    43
    Sorry to say it sounds like the latince hasn't been removed.
    Anhydrire is fairly new to the domestic building trade and unfortunately some tilers and flooring men are being caught out with this.
    Some are saying it upto the builder to remove the latince, either way the flooring contractor should have checked before fitting.
     
  18. Rugmunching

    Rugmunching Well-Known Member

    3,679
    630
    113
    Time to get the whole lot dug up and start from scratch...
    Wonder who is going to fork out for this one :eek:
     
  19. merit

    merit Well-Known Member

    8,003
    1,640
    113
    Anhydrite takes ages to dry out too!! It dries patchy and from the top down. I'm sure the heating would of helped dry it but from my experience it's a long wait untill fully dry
     
  20. pf flooring

    pf flooring Well-Known Member

    1,600
    602
    113
    will fall up mostly, grind the top check its dry and try again :)
     